Object | Definition |
Devices | A device is any “thing” that Indigo can interact with - usually it's some kind of hardware (light switch, appliance module, motion sensor, etc), but devices can also be other non-hardware things (iTunes server, calendar, etc). |
Triggers | A trigger is generally some kind of “event” that occurs. Indigo can use that event to execute actions in response. |
Schedules | A schedule is similar to a trigger, but the event that causes the execution of the actions is a temporal event of some kind. Either a fixed point in time (5/2/2011 at 1:00pm) or more likely some repeating time (every day at 1:00pm). |
Action Groups | Action Groups are collections of actions that may be reused (and modified) easily between multiple triggers, schedules, and control pages and executed via various clients (the Mac Client, the Indigo Web Server (IWS) web pages, Indigo Touch, etc). |
Control Pages | Control Pages are user-created interfaces to control their Indigo system - for instance you could create a graphical floor plan with light icons in the various rooms. |
Variables | A variable is a place where your home automation logic can store information that changes during the normal operation of your home and that can be used in other parts of your system: for instance, you can have a variable that represents whether your home is occupied or not - then you can have special automation logic that takes place when that variable changes. |
Here is the device dialog:
The first thing that you need to select is the Type
. Indigo includes support for the following device types: Z-Wave, INSTEON, and X10 (click on the types for details of how to manage devices of that type). Indigo also has a Virtual Devices interface type and the following plugins which add additional device types:
If you add other 3rd party plugins that supply devices, they will show up on the Type
menu as well. There are over 95 3rd party plugins listed on our Plugin List that cover many other types of devices, including alarm panels, media servers, A/V equipment, and much more. If you're a programmer and would like to develop plugins, check out our technical documentation section for all the docs you need to get started building Indigo plugins.
Once you've selected a device type, the fields and buttons between the Type
popup and the tab view at the bottom of the screen will adjust based on the type of device that you select. The tab view will show at least one tab (titled “Settings”) for every device. Here's an example of a Z-Wave module:
Inside each tab, you have the Name
field, which represents the unique name of this device. Next you have the Notes
field - it's a free-form text field that you can put anything into you want - perhaps to help describe what features you're using, where it's physically located, or significant triggers that use it. You can put whatever you like in that field.
Enable Indigo communication
checkbox - this is useful if you have a device that you're temporarily taking out of service or moving. If you uncheck this checkbox, Indigo will not attempt to communicate with it in any way - so you won't receive errors in the Event Log when any action is taken for this device.Display in remote UI
checkbox which, as it says, lets you see this device in remote client applications. Some devices have multiple “personalities” - in other words a single physical device can actually represent multiple devices. The INSTEON FanLinc is one example: it's a single module that has Fan Speed controls and Dimmer controls. In Indigo, each of these is represented as a different device in the various device lists. However, when you edit one of them, each device will be represented in a single dialog with multiple tabs:
Use the Type Device State Changed
to trigger an action whenever a device's state changes. For example, you could create a Trigger Action for whenever a specific light's brightness becomes greater than 75% or for when your thermostat's temperature drops below 55 degrees.
Use the Type Variable Changed
to trigger an action whenever an Indigo variable value changes. Variable values can change as a result of a Modify Variable action or from the user directly modifying the value. See the Variables section for more information about using variables.
Note: becomes true
will fire when the value becomes “true”, “on”, “yes”, and “1” (if it wasn't one of those values previously). becomes false
will fire when the value becomes “false”, “off”, “no”, and “0” (if it wasn't one of those values previously). Any other value will be neither true nor false and neither will fire.
Use the Type Email Received
to trigger an action based on emails sent to Indigo. You can trigger an action if any email is received, or restrict the trigger to emails that contain phrases within the subject title and/or specific sender email addresses. See the configuring email settings section for more information about having Indigo send and receive emails.
Use the Type Indigo Server Startup
to trigger an action when the Indigo Server process is first launched.
Use the Type Power Failure
to trigger an action whenever the computer interface detects a power failure. For Indigo to receive this information from the computer interface, the computer running Indigo must be connected to an uninterruptible power supply (UPS). Otherwise, the command from the interface will be sent to a computer with no power.
Use the Type Interface Connection Initialized
to trigger an action whenever the communication between Indigo and the interface is successfully started.
Use the Type Interface Connection Failure
to trigger an action whenever the communication between Indigo and the interface fails. An unplugged USB cable or a malfunctioning interface can cause this error.
Use the Type INSTEON Command Received
to trigger an action when INSTEON commands are sent from a device, like a KeypadLinc, and then received by the PowerLinc interface. Select the INSTEON command from the Received
popup that you want to cause the trigger, along with the Device
from which the command was sent. For devices with multiple buttons, like the KeypadLinc and ControLinc, you can also choose which button press causes the trigger via the Using button
popup.
TIP: The Double Tab On
and Double Tap Off
command types are useful for triggering lighting scenes at a wall switch (like the SwitchLinc). For example, you could create a Double Tap Off
trigger action that turns off all the lights in the house when a SwitchLinc near the back door is pressed twice.
Use the Type Z-Wave Command Received
to trigger an action when Z-Wave commands are sent from a device, like a scene controller or motion sensor, and then received by the Z-Wave interface. Each device type will have different options based on it's capability
Use the Type X10/RF Command Received
to trigger an action when X10 commands are sent from a device, like a PalmPad, SwitchLinc 2-Way Dimmer, etc, and then received by the X10 or RF interface. Select the X10 command from the Received popup that you want to cause the trigger, along with the Device
or X10 Address
for that command.
Choose A/V Button Pressed
from the Received
popup to trigger an action using one of the X10 universal remote controls, such as those included in the X10 “Entertainment Anywhere” kits.
Plugins may define events as well - these will be listed below the X10/RF Command Received
event in the Type
popup.
As with trigger dialog, the schedule dialog has 3 tabs: Schedule
is for specifying the temporal settings; Condition
is for specifying further conditions that can determine if the actions are executed, and finally the Actions
that will execute. Conditions and Actions are discussed in a later section. The two main sections of the Schedule
tab separate the temporal settings into two parts - the time of day and the date.
The Time
section allows you to specify the time of day that the schedule will execute. There are 4 main options:
Customize
button (see image below):At sunrise
is the default (0 is inserted into the text box on the main dialog)minutes before sunrise
(-X is inserted into the text box on the main dialog)minutes after sunrise
(X is inserted into the text box on the main dialog)Force trigger time to Y at the earliest
will cause the trigger to execute at the specified time if the minutes before sunrise specification is earlier than YForce trigger time to Y at the latest
will cause the trigger to execute at the specified time if the minutes after sunrise specification is later than Y
You can also randomize all of the above settings by entering a non-zero value in the Randomize by
text box. Each execution will add the randomized amount of time. Use this setting to create schedules that have that “lived in” look.
There are two options at the bottom of the dialog. The first is Hide executions in Event Log
which will suppress any log messages indicating that this schedule has executed. This especially useful for schedules that repeat very frequently (every X minutes for instance). The second is Automatically delete after next execution
which will do exactly that - after the next time that the schedule executes it will be deleted regardless of the time or date settings.
On any dialog that has an area where you select actions (Triggers, Schedules, Action Groups, and Control Pages), The first thing you'll see is the Type
popup:
The Device Actions
category has 7 subcategories. Plugins can also add a submenu to this category for the actions they define that work directly on devices. By default, Indigo ships with the Airfoil Pro, iTunes and Timers and Pesters plugins, which add subcategories to this menu. You may have other menus as well if you've installed 3rd party plugins.
Request Full Status Update
- ask the device to reply with all possible status information. This is dependent on the capabilities of the device.Request Energy Update
- ask the device to reply with only it's energy usage information. This is dependent on the capabilities of the device - many do not support energy monitoring.Reset Energy Usage
- ask the device to reset the running total of energy usage. This is dependent on the capabilities of the device - many do not support energy monitoring.Turn On Keypad Button
- turn on the specified button' light on the device. Only applies to devices which have separate buttons that indicate state with a light.Turn Off Keypad Button
- turn off the specified button'light on the device. Only applies to devices which have separate buttons that indicate state with a light.Beep Device
- ask the device to beep. This function is dependent on the capabilities of the device.These controls are for lights and on/off (sometimes called relay) devices.
All Off
- turn off all light and appliance devices. The Devices:
popup lets you select All INSTEON/X10
, All INSTEON
, All X10
, or a specific X10 house code.All Lights On
- turn on all light devices with the same Devices:
options as All Off
All Lights Off
- turn off all light devices with the same Devices:
options as All Off
Turn On
- turn on a specific device with an optional complementary Auto-off after X minutes
actionTurn Off
- turn of a specific device with an optional complementary Auto-on after X minutes
actionToggle On/Off
- turn on the device if it's off or off if it's onSet Brightness
- set the brightness of a lamp device to a specific percentage (from 0-100)Brighten by %
- increase the brightness of a lamp device by a specific percentage (from 0-100)Dim by %
- increase the brightness of a lamp device by a specific percentage (from 0-100)Match Brightness
- set the brightness of any number of dimmer devices to the value of the selected dimmer device - so you can quickly and easily create a very simple scene.Set RGBW Levels
- set the RGBW levels for lights that support setting their color.
Run Schedule
- selecting this action will show you the zone table (shown above) that will allow you to set the duration for each zone and optionally multiply those durations by the selected variable. This last option is useful if you change durations based on time of year - you can change the variable value but keep the existing schedule and it'll adjust the duration as appropriate.
Pause Schedule
- this action will pause the current schedule (if for instance you're walking to your car and don't want to get wet)Resume Schedule
- this action will resume a previously paused schedule (once you're in your car)Stop (all zones off & clear schedule)
- this action will completely stop the scheduleActivate Previous Zone
- this action will cause the schedule to back up one zoneActivate Next Zone
- this action will cause the schedule to jump to the next zoneTurn on Specific Zone
- this action will turn on a specific zone for the maximum run time specified in the sprinkler's definition and will turn off after it's done
Set Heat Setpoint
- set the heat setpoint to an absolute temperatureIncrease Heat Setpoint
- increase the heat setpoint by some number of degreesDecrease Heat Setpoint
- decrease the heat setpoint by some number of degreesSet Cool Setpoint
- set the cool setpoint to an absolute temperatureIncrease Cool Setpoint
- increase the cool setpoint by some number of degreesDecrease Cool Setpoint
- decrease the cool setpoint by some number of degreesSet Mode
- set the mode of the thermostat to one of the following:All Off
- set the HVAC unit so that both heat and cool setpoints are ignored - the unit will not come on at allHeat On
- activate the HVAC unit so that only the heat setpoint is usedCool On
- activate the HVAC unit so that only the cool setpoint is usedHeat/Cool On
- activate the HVAC unit so that both heat and cool setpoints are usedRun Heat Program
- tell the thermostat to run the heat program that is programmed directly into the thermostat (see the thermostat documentation for details)Run Cool Program
- tell the thermostat to run the cool program that is programmed directly into the thermostat (see the thermostat documentation for details)Run Heat/Cool Program
- tell the thermostat to run the heat/cool program that is programmed directly into the thermostat (see the thermostat documentation for details)Fan Auto On
- set the fan so that it only runs as neededFan Always On
- turn the fan on so it'll continuously runGet All Status
- get all information from the thermostatGet Current Mode
- get the current modeGet Ambient Temperature
- update the temperatureGet Ambient Humidity
- get the humidityGet Setpoints
- get the setpointsCycle Through Thermostat Modes
- this will allow you to easily cycle through thermostat modes in this order: Off, Cool, Heat, Auto. Especially useful in conjunction with the “Thermostat Mode+.png” image on a control page - just add this as a server action and you have a simple control for adjusting the thermostat mode - each time you tap/click the image, the thermostat selected will cycle to the next mode just like pressing the Mode button on the thermostat itself (if it has one).Toggle Thermostat Fan Mode
- like the action above, this method will toggle between the two fan modes: Fan On (always on) and Fan Auto (automatic). Again, useful with the “Thermostat Fan Mode+.png” image file.v1 INSTEON thermostat adaptors didn't broadcast out changes to update it's internal state representations for the thermostats - which is why there are so many options to get status. Indigo 7 catches the v2 thermostat update broadcasts so the need to manually get updates should be reduced.
Set Fan Speed
- set the speed of the device to a specific levelIncrease Fan Speed
- increase the fan speed by some # of units - for instance, on a FanLinc that's currently on Low
, increasing the fan speed by 1 will set it to Medium
Decrease Fan Speed
- decrease the fan speed similarly to the above Increase Fan SpeedTurn Fan On (resume last speed)
- this will turn the fan on to it's last speed settingTurn Fan Off
- turn the fan off completelyToggle Fan On/Off
- toggle between on and offCycle Through Speed Control (FanLinc) States
- use this action to cycle through the fan speeds in this order: High, Medium, Low, Off. It's basically an electronic version of pulling the fan's chain.
Turn On Output
- turn on the specified outputTurn Off Output
- turn off the specified outputTurn Off All Outputs
- turn off all outputsGet All Status
- get the status of all inputs and outputsGet Binary Outputs Status
- get the status of all the binary outputsGet Binary Inputs Status
- get the status of all the binary inputsGet Analog Inputs Values
- get the voltage value of all the analog inputsGet Sensor Inputs Values
- get the value of the 1-wire sensor bus (only available on some I/O devices)There are a few controls specific to Virtual Devices:
Update Device Group Saved State
- updates the saved state of all devices in a device group so the next ON command will match their current settings.Set Virtual On/Off Device State
- explicitly sets the state of a virtual on/off device. Useful if the state gets out of sync or is not maintained by a variable.There are a few controls specific to certain brands of devices:
Note: in versions earlier than Indigo 7.2, these commands are on the Insteon Actions menu described below.
Set LED Brightness
- set the brightness of the LEDs on certain devices. Newer KeypadLincs are supported as well as some SwitchLinc models. Unfortunately there isn't really a way to tell you which devices are supported so you'll just have to try it and see if it works. Turn On/Off KeypadLinc Buttons
- turn on/off groups of buttons. Why not just have multiple actions using the built-in Turn ON/Turn OFF LED actions? Because each of those requires a lot of INSTEON traffic - and if you need to set several buttons at once this action will do it in one (or two if you want to maintain some buttons) action(s). It's more efficient and easier to configure (one action versus potentially seven actions). Select the action you want to take for each button: Turn On
, Turn Off
, Leave Alone
. The latter option will require that we query the KPL to find the states first so if you select that for any of the buttons the action may execute a bit slower than it would otherwise. Note: using this action, which is sending raw INSTEON commands through the IndigoServer, will cause the KeypadLinc's button states in Indigo to become out of sync. This is because the server doesn't know that you're changing the button states given that it's just a raw command message that it's being asked to send to the PowerLinc. If you need to keep the states in sync then add another action to do a status request to the KeypadLinc (after a short delay to avoid collisions).Set KeypadLinc Auto-Off Button Group
- specify what buttons will go off automatically when you press any other button. Useful in conjunction with Toggle Mode below for creating “radio groups”. See the FanLinc and KeypadLinc article for usage examples. Set KeypadLinc Button Toggle Mode
- specify whether a button toggles (alternates between ON and OFF when pressed) or whether it sends a single command anytime it's pressed (can send either ON or OFF). Useful in conjunction with Auto-Off groups above for creating “radio groups”. See the FanLinc and KeypadLinc article for usage examples. Set Motion Sensor LED Brightness
- set the brightness of the LED that flashes inside the motion sensor when motion is detected. While the brightness value is between 0 and 255, 0 does not mean the LED is completely off - it's just very dim. Note: only revision 2 Motion Sensors with jumper 5 set can be configured.Set Motion Sensor Timeout
- set the timeout value between the time the motion sensor stops detecting motion and when it sends the OFF command. The timeout values work like this: 0 is equal to 30 seconds and 255 is equal to 2 hours. Values in between are proportional to those values. Note: only revision 2 Motion Sensors with jumper 5 set can be configured.Set Motion Sensor Day/Night Sensitivity
- set the sensitivity for when the motion sensor detects changes from dawn to dusk and vice versa. The sensitivity values work like this: 0 will make the sensor register day all the time and 255 is equal to night all the time. Values in between are proportional to those values. Note: only revision 2 Motion Sensors with jumper 5 set can be configured and Motion Sensor II models will interpret 0 as 3.Set I/O Linc Momentary Mode
- set the momentary mode of an I/O Linc to A, B, C, or None (the built-in UI only sets A or None). Configure SynchroLinc
- configure the Trigger Watts, Threshold Watts, and Delay Seconds in a SynchroLinc. Here are the details of those settings:New in Indigo v7.2+ are the following actions that are specific to HomeSeer switches:
Set LED Mode
- set the mode of the LEDs on the switch. The default Normal (load status)
behavior is for them to represent the brightness to which the switch is set. You can set the switch to Status (custom status)
which will allow you to individually turn on and off each LED and set it's color. You can also set the bottom LED's behavior.Set LED Color and On/Off State
- when the switch is in Status
mode, you can use this action to turn on/off and set the color of any of the LEDs.Set LEDs Blinking Behavior
- start/stop LEDs from blinking.
The Server Actions category has three actions and three subcategories.
Remove all delayed actions
- this will remove all delayed actions regardless of delay typeRemove for device
- remove any delays for the selected deviceRemove for trigger
- remove any delays from the selected triggerRemove for schedule
- remove any delays from the selected scheduleThis action will attempt to reset all built-in hardware interfaces. There are no options.
The Execute Script
action allows you to execute either a Python or AppleScript as an embedded script or stored in a script file. In general, you should use embedded scripts for scripts that are short and very quick to execute.
Embedded Python scripts will be limited to 10 seconds of execution time - if they run longer than that they will be killed. If you have a Python script that is a long running script you should save it in a separate file and execute it from the file by selecting the File radio button then selecting the file. Python scripts executed from files are executed in their own process and are therefore much less likely to adversely effect the server process if they don't work as expected.
Embedded AppleScripts must run on the server's main execution thread so if it delays, can hang on external events like network access, or otherwise does a lot of processing, then everything else in the server will be put on hold until the script is finished. Therefore, you definitely should keep embedded AppleScripts very simple. As with Python scripts, long running AppleScripts should be stored in a separate AppleScript file (created with Script Editor) and executed that way - external AppleScript files execute in their own process and are therefore much less likely to adversely effect the server process if they don't work as expected.
For embedded scripts, you can click the Compile
button and we'll do our best to check the script for syntax errors. Click the Run
button to have the script executed immediately.
This will run the specified script file optionally with the output being inserted into the specified variable. The script must be marked executable and a valid shebang (#!/path/to/shell) must be specified at the top of the script. Note - this won't work for AppleScripts - you should use the built-in Execute Script action and select the script file that way. Also, if you're running a Python script you'll probably just want to use the Execute Script action since script files run from this plugin won't have access to the IOM (import indigo
, which is Python-only).
This action will send an email to the specified email addresses that contains the specified number of lines from the log file. This is useful for debugging problems (among other things). Tip: this action is also available interactively by selecting the Help→Email Log…
menu item.
This action will enable Indigo communication with the selected device. You can specify an optional complementary Auto-disable after X minutes
action.
This action will enable processing of the selected trigger. You can specify an optional complementary Auto-disable after X minutes
action.
This action will enable processing of the selected schedule. You can specify an optional complementary Auto-disable after X minutes
action.
This action will disable Indigo communication with the selected device. You can specify an optional complementary Auto-enable after X minutes
action.
This action will disable processing of the selected trigger. You can specify an optional complementary Auto-enable after X minutes
action.
This action will disable processing of the selected schedule. You can specify an optional complementary Auto-enable after X minutes
action.
There are three actions that are specific to variables.
This will insert the selected state of the selected device into the specified variable. After you specify the device, click the Edit Action Settings…
button and it will open a dialog (shown above) with a list of all possible states for the device you selected and a popup of all variables. You can create a trigger that executes when a device's state changes and have it insert the new state into the variable.
Click the Edit Action Settings…
button and it will open a dialog (shown above). Here you will select the variable and, optionally, the format string as defined in the Python datetime string formatting documentation (see the chart at the bottom for format specifiers). The format in the Format string
field is the default format.
button and it will open a dialog (shown above). Here you will select the variable and the values that will be toggled. The first 4 options (true/false
, on/off
, yes/no
, enabled/disabled
) on the Toggle values
menu are self explanatory (although note that values will be converted to lower-case for comparisons). The last option, Custom Values
, will allow you to specify the values. We will first try to match the custom variables without converting to lower case (some unicode characters behave oddly when lowercased) and if we don't find a match then we'll convert. Finally, if nothing matches, we'll just set the value to the first value.
button and it will open a dialog (shown above). Here you will select the destination and source variables.
In the standard install of Indigo, there are two actions: Send Email and Growl Notify. Plugins are allowed to add menu items to this category so there may be more options if you've installed some 3rd party plugins.
Note: In versions earlier than Indigo 7.2, the menu items in the Insteon Brand Specific Controls menu were in the above menu.
Scene On
- send the ON command to every device in the group - if the device has an adjustable ramp rate and/or brightness value, those are honoredScene Instant On (to 100%)
- send the ON command to every device in the group - but ignore ramp rates and default brightness values (everything comes on full immediately)Scene Off
- send the OFF command to every device in the group - if the device has an adjustable ramp rate it will be honoredScene Instant Off
- send the OFF command to every device in the group - ignore ramp rates (everything goes off immediately)
The Scene:
popup represents the INSTEON scene number - any name that you've assigned to that scene will also show up in the text field beside it (you can change the name there also if you like). Use the Send On
and Send Off
buttons to test your scene commands.
Finally, if you need to add, modify, or delete a device from the scene, click on the Modify this Scene…
button. See the Indigo and INSTEON Link Management page for more details.
There are three options to each action (and in fact are the only configurable options if you select None
as the action Type:
Delay by hours:minutes:seconds
- this will delay the execution of the action by some amount of time (not over 24 hours)Override previous delay
- this will automatically delete any previous delays specified for the action aboveSpeak
- if you enter text in the text box Indigo will use the voice synthesis to speak the text
Use the Add New
button below the Speak:
text area and the separator if you would like to add an additional action. You can then use the Prev
and Next
buttons to select which action's settings are being displayed. Press the Show All
button to see a list of all the actions:
You can then Duplicate or Delete the selected action, or use the Up
/ Down
buttons to reorder the list of actions. To edit a specific action's settings, double-click on the action or press the Edit…
button.
To create a new action group:
Action Group List
from the View
menu.New…
button at the top of the main window.Name
the group, for example “going to bed.”Notes
.Type:
and select the various options. (See the actions section above for details on all of the action's settings, and information on managing multiple actions to the Action Group)
Indigo includes a built-in Web server that allows remote execution of your Action Groups from Indigo Touch or any modern Web browser (Safari, Firefox, Opera). Follow the instructions in the Starting Indigo Server section of the Getting Started guide to make sure that the following options are enabled: Start and connect to Indigo Server on this computer
, Allow remote access
, and Enable iPhone, iPod touch, and remote Web browser access
The Display in remote UI
option at the bottom of the dialog will make this action group show up in remote clients like Indigo Touch or the web pages. When you see them in those UIs you can tap/click the action group and it will be executed so it's an easy way to control scenes from those clients.
To create a new Control Page, select View→Control Pages
, then click the New…
button above the control page list. You will be shown the control page editor window:
The editor window has 4 areas - the first is the the global control area. In this area you'll find buttons to create new page elements (labels, controls, etc), duplicate existing elements, delete elements, and turn on/off some features of the editor. Select Snap to grid
to have page elements snap to a grid that overlays the design area (see the next item). Select Show grid
to show the aforementioned grid. Select Edit z-order to show you the order of the page elements and allow you to change them. Higher numbered elements are drawn last, so if you have overlapping controls the one with the highest order will be drawn last.
The white area is the visible area that you'll see on the web page or in Indigo Touch. The gray area is just the image border area - items in the gray area will not show on the control page. If you have the Edit z-order
checkbox described above checked, you'll see controls like this for each page element:
In the example above, you see 4 page elements: the graphical server status element, the server status text area, a device state element using a ceiling fan image, and another device state element using a lightbulb image. The ceiling fan element is selected, as you can tell by the blue brackets at each corner of the image. Because I also have the z-order checkbox selected, you see the z: #
next to each element, and above and below that for the selected element you see up/down arrows, one with a line above/below and one without. The arrows that aren't pointing to lines will move the element up/down one step at a time. The arrows that point to lines will move the element to the top/bottom of the element hierarchy.
This is where you set global information about the page itself. The Page Name:
and Description:
fields are pretty self-explanatory. Check the Hide Tab Bar at bottom of Indigo Touch when shown
to have the bottom navigation bar hidden when this page is viewed in Indigo Touch. You can use a Background image:
by selecting it from the popup, such as a floorplan or other image. You can add your own image by creating a PNG file and adding it to the backgrounds folder (to open that folder in the Finder just click the Show Folder
button - and if you add an image while Indigo is running, click the Refresh
button to have it added to the popup). Note: some versions of Indigo 7 don't like spaces in the background image name so just replace spaces with another character such as an underscore.
If you aren't using a background image, your background image is smaller than the total size of the page, or if your background image has transparency identified, you can specify the color of the rest of the background by clicking on the Background color:
colorwell. Finally, you can have the page size constrained to the size of the background image or you can specify your own page size. Here are a few design tips for designing pages for Indigo Touch on various devices:
The final section is the bottom control area - the Help
, Cancel
, Browser Preview
, and Save and Close
buttons are also pretty self-explanatory (the Help button may have gotten you to this page in fact).
When you select Device State
from the Display:
popup, you're shown a list of devices in the For:
popup. Once you've selected a device, the next popup will show the list of states for that device.
The next row of options is for the Caption:
field - static text that can be used as a label for the control. It can be placed on any side of the control (left, right, above, below) as well as centered on top (good for buttons).
The next two options, Client action:
and Server action:
allow you to specify what happens when the control is interacted with (via click or tap) and are describe in separate sections below.
Variable Value controls have the exact same options as device state controls, but rather than use the device state it uses the value of the variable you selected in the For:
popup to select the correct image or as the text to display.
Refreshing Image URL controls allow you to specify a URL to an image that is refreshed periodically (specified in the Refresh rate:
popup). Just specify the image size, URL, and refresh rate.
Open in new window
checkbox really only effects viewing pages in a browser, not Indigo TouchOpen in new window
checkbox is checked).In Indigo Touch, it will cause Mobile Safari to open and show the page specified by the URL.Every page element may also have server actions performed - these are the typical actions described above. Just like Triggers and Schedules, you can specify a single action or multiple actions.
Variables are used to hold information that can help your home automation logic. For instance, Indigo ships with an AppleScript which stores weather information in variables. You can use that information to display on control pages, as part of your conditional logic (see Conditions below), or as a trigger for some other action.
To manage your variables, select Window→Variable List
and you'll see the Variable List window:
The middle section is the actual variable table. It actually has two parts: the table header and the table itself. If you right click on the table header, it will allow you to customize what columns show up in the table. To change a variable Name
, just double click on the name and type in a new name. Note that variable names can contain only alpha-numeric characters and underscores “_” and must be unique. Variable values may contain pretty much anything and can be changed by double-clicking on them.
The Remote Display
column indicates whether a variable will be shown in the built-in variable list in remote clients. The ID
column shows the unique identifier for the variable - you'll need this if you're planning on writing Python scripts.
If you right-click a variable, you can toggle the Remote Display attribute or copy the variable id to the clipboard (for easy pasting into scripts). You can also select the Show Dependencies
option to open a window that shows all other objects that are dependent on that variable. See Deletion Dependencies for more information.
The bottom section are the folder control buttons. Clicking on the plus (+
) will add a new folder, and clicking on the minus (-
) will delete the selected folder. If the folder isn't empty when you try to delete it, a sheet will come down prompting you to decide if you want to delete all the enclosed variables or if you want to move them out of the folder first. If you right click on a folder in the list, you can toggle whether the folder shows up in remote clients and you can copy the unique folder id to the clipboard for use in scripts.
On the Trigger and Schedule dialog, there's a tab named Condition
. If you select this tab, you'll see something like this:
Conditions allow you to specify extra logic that's evaluated at execution time to determine if the actions associated with the trigger or schedule should be executed. Most conditions will be set to Always
- in other words, there are no additional conditions associated with the trigger or schedule. However, there are many situations where you need to factor in other information at execution time that can help determine if the actions should be performed.
This is a negative condition - if None
of the rules are true then the actions will execute. It could also be written as an All
rule if you switched the tests around:
This version says that if All
the conditions are true (windows aren't open, temperature is greater than 40, and rain total is less than 3/4 of an inch) the actions will execute.
Note for variable comparisons: is true
will evaluate true if the value is one of these: “true”, “on”, “yes”, and “1” and will evaluate false if it's anything else. is false
will evaluate true if the value is one of these: “false”, “off”, “no”, and “0” and will evaluate false if it's anything else.
"All" "of the following rules are true" "If dark" "Any" "of the following rules are true" "If current date" "is between" 8/1 "and" 8/31 "If variable" houseMode "is equal to" "value" "away" "None" "of the following rules are true" "If variable" test1 "is equal to" "variable" test2 "If variable" test3 "is between" "5" "and" "10"
If, however, you still can't express your conditional logic using the rule editor, you can still select the If script returns true:
radio button and write a script that returns true or false.